jbuzz
- United States
and 408.36 does not say that IMO.IMO no unless it a listed method provided by the manufacturer.
(D) Back-Fed Devices. Plug-in-type overcurrent protection
devices or plug-in type main lug assemblies that are
backfed and used to terminate field-installed ungrounded
supply conductors shall be secured in place by an additional
fastener that requires other than a pull to release the
device from the mounting means on the panel.
I guess it depends on what the inspectors or AHJ calls a "fastener".
At least works better than a method many guys use here. We just put a head of screw on a breaker so it looks like there was a bolt down kit installed.
That section reads to me like they are referring to the circuit breaker, not the fasting means. I.e.: The overcurrent device must be secured so that a pull cannot remove the overcurrent device from the mount.Most cases a zip tie installed this way could be worked loose by pulling it up over the top of the breakers.
No we call it Securing..Tie wraps are used often to fasten MC cable.
That's where my problem exists, a cable tie doesn't cut it.
UL 67 Panelboard and Switchboard Accessories - Component
The devices covered under this category are incomplete in certain constructional features or restricted in performance capabilities and are intended for use as components of complete equipment submitted for investigation rather than for direct separate installation in the field. THE FINAL ACCEPTANCE OF THE COMPONENT IS DEPENDENT UPON ITS INSTALLATION AND USE IN COMPLETE EQUIPMENT SUBMITTED TO UL.
USE
This category covers incomplete panelboard assemblies, such as panelboard interiors. Also covered under this category are accessories intended for use with panelboards or switchboards, such as branch circuit buses for circuit breakers and switches, insulators, anti-turn devices, neutral assemblies, bonding kits, equipment grounding bars, barrier kits, back-fed unit hold-down kits, transfer kits for optional standby power systems , and the like.