jbuzz
Member
- Location
- United States
Would a panel used as service equipment that is installed as main lugs be considered on the supply side of Service disconnecting means as it pertains to this code. Basically I have a 100 Amp service with a 4 space load center directly below the meter, the premises are fed by a 2-100 breaker and I used the other two spaces to feed/backfeed a Utility interactive system. Now the inspector says i have to comply with 705.12 (D). I disagree but figured I would take it up with you guys.