chris kennedy
- Miami Fla.
- Retired electrician
Blue highlight below is the commentary, red is the point of interest.
(C) Boat Hoists. GFCI protection shall be provided for
outlets not exceeding 240 volts that supply boat hoists installed
in dwelling unit locations.
The proximity of this type of equipment to water and the wet
or damp environment inherent to the location in which boathoists are used is the reason for this GFCI requirement. Documented
cases of electrocutions associated with the use of
boat hoists compiled by the U.S. Consumer Product Safety
Commission substantiated the need for this requirement.
The requirement applies only to dwelling unit locations, and
GFCI protection must be provided for boat hoists supplied
by 15- or 20-ampere branch circuits rated 240 volts or less.
It is important to note that in contrast to the requirements in
210.8(A) and (B), 210.8(C) applies to all outlets supplied
from 15- and 20-ampere, 120-volt branch circuits, not just to
receptacle outlets. Therefore, both cord-and-plug-connected
and hard-wired boat hoists are required to be GFCI protected.
So my question is, where in 210.8 would the commentary authors find this requirement applies only to 15-20A hoists?
30A and I don't need GFCI?
Thanks