If memory serves me correctly, a linear accelerator may be calibrated every once in a while, when it will run at full power for 3 hours or more.
Standard X-ray is a fraction of a second. There are demand factors you may use in 517. I believe its 50% for the first unit.
I believe a MRI should be considered a continuous load.
C-T's are basically an xray unit - but it's more like taking an xray movie than a single photo. Every one I have ever seen lists a peak demand, and a continuous long term rating. I apply x-ray demand factors to the peak ratings, and a continuous load demand factor (1.25) to the continuous rating, and I make sure my distribution can handle both.
Normally, you should get a detailed site installation package from the vendor. That usually includes typical installation drawings, and specifications. Then they will follow up with site specific drawings. We use these to produce our construction drawings, which include connections to the facilities electrical distribution.
Some of these companies have these generic installation drawings available on-line. GE does. (But be careful - they may not be up to date, and there may be small differences in the equipment that make a big difference in the power consumed.)