When sizing an Equipment Grounding Conductor, is the following true:
Single Conduit fed from I-Line Circuit Breaker 480V 3-Phase, the Ground conductor should be sized based on the I-Line CB rating. For instance, a 600Amp CB would require at minimum a #1 copper ground wire.
If the feed is a parallel run in 2 conduits from a single I-Line CB, the ground conductor is still size base on the CB size not on the ampacity of the conductors. For instance, a 800Amp CB feeds a panel with (2) conduits. Each Ground conductor would a 1/0 or larger copper cable, not sized based on the current carrying conductors.
If there are multiple circuits in a single conduit, 1 Grounding conductor is permitted if it is sized to largest over current protection. For instance, 3 circuits (20A, 40A and 50A) are all in a single conduit, a single ground conductor of #10 or larger is permitted.
Single Conduit fed from I-Line Circuit Breaker 480V 3-Phase, the Ground conductor should be sized based on the I-Line CB rating. For instance, a 600Amp CB would require at minimum a #1 copper ground wire.
If the feed is a parallel run in 2 conduits from a single I-Line CB, the ground conductor is still size base on the CB size not on the ampacity of the conductors. For instance, a 800Amp CB feeds a panel with (2) conduits. Each Ground conductor would a 1/0 or larger copper cable, not sized based on the current carrying conductors.