New to the Forum, thanks to Mike and all that make it possible.
I live in Florida and had the local electrical company here this week to put in underground service to a new pole barn I am building on our property. It will have a 200 amp service and they ran 4/0 Aluminum 269' from the transformer that was set 3 years ago when we renovated our house.
My question relates to the wire size they ran to the house during the renovation that has a 400 amp meter socket and 2-200 amp panels. When I was watching them pull the wire into the transformer ( this week for the pole barn ) I noticed that the wire size that ran to the house was smaller than the 4/0 they had just pulled to the pole barn. Shouldn't it be at least 4/0 maybe larger for the 400 amp service?
This may also be the answer to an issue we have had since the completion of the house. When either of the air conditioners start up the lights in the house dim for a moment. This is particular annoying since I asked my electrician to up the wire size for any lighting circuit to #12 to avoid this happening. I have had 2 other HVAC companies check the units and both said they were fine and wired with the proper size wire.
My guess at this point is that even though you get an acceptable voltage reading when checking any wire the voltage drop under startup load is to much for the wire from the transformer to the meter socket. The entrance cable to both panels is 4/0 aluminum. One has a run of 8' and the other has a run of 30' to the automatic transfer switch for a future generator and then 30' to the second panel.
I'm I thinking in the right direction or am I missing something.
Thanks Brad
Thanks Brad