What about the rapid-shutdown initiator? NEC 690.12 does not specify where you should locate the initiating device or what type of device you must install. This lack of detail is intended to provide system integrators and AHJs with the flexibility to adapt rapid-shutdown solutions to the complexities of the built environment. While the best location for a rapid-shutdown device and the required label is typically at or near the service equipment, the fire service may have preplanned emergency response tactics for some large commercial or industrial buildings that favor a different location.
One of the simplest ways to initiate rapid shutdown is to set it up to occur automatically upon loss of ac power. This is why NEC 2014 does not require a specific type of rapid-shutdown initiation device. If you install a roof-mounted residential microinverter system or a commercial PV system using roof-mounted string inverters located within 10 feet of the array, you do not need any special equipment to initiate rapid shutdown; you can accomplish this function simply by interrupting utility-supplied power to the inverters. Some companies have developed various rapid-shutdown switches, and claim that rapid shutdown requires these extra switches. However, you have to install an extra rapid-shutdown switch only when you need to turn the array off by some means other than loss of utility power, as with battery-backup systems or inverters equipped with a daytime backup-power outlet.
NEC 690.12 does not specify how many buttons, switches or movements of the hand are allowed to complete rapid shutdown. Ideally, the process should only require one action. As written today, however, the language in 690.12 provides system integrators and AHJs with the flexibility to consider alternatives. Note that if the system design requires more than one action to initiate rapid shutdown, the 10-second time limit still applies. Therefore, where systems are deployed with more than one initiation device or switch, they should all be in close proximity so that emergency personnel can de-energize all of the PV system circuits on the building within 10 seconds. Further, labeling must clearly identify all of the initiation devices and all of the steps required to complete rapid shutdown.