jamie300993
- United Kingdom
Hi,  If possible, I would like someone to clarify whether or not I am correct in my calculation of the voltage drop for a three phase Dyn Transformer?
The transformer in question is a 3MVA 11kV/415V Dyn Transformer which has the following p.u. R & X values:
R = 0.00355pu = 0.355%
X = 0.0901pu = 9.01%
If I want to calculate the secondary voltage drop, and the load power factor is 0.85 with a Primary transformer current of 55A, would the following be correct;
IPrimary (Phase) = 55A
Secondary Phase current = Line Current (Secondary is star connected ) = 55*(11000/415) = 1457.83A
Converting X & R to ohms:
R(ohms) = (10*%R*kVsecondary2)/kVA = (10*0.3555*0.4152)/3000 = 0.0002038?
X(ohms) = (10*%X*kVsecondary2)/kVA = (10*9.01*0.4152)/3000 = 0.0051725?
? = cos^-1(0.85) = 31.788?
Volt Drop = Sqrt(3) * 1457.83 * (0.0002038*0.85 + 0.0051725*sin(31.788)) = 7.32V
Does this mean that the voltage to the load will be 415-7.32 = 407.68V?? This is the bit I would like confirming if the remainder of the calculations happen to be correct?
Many Thanks in advance for any help