jeff owens
- lasd vegas, nevada
don't ask me why, but an engineer designed and had installed a remote indication for emergency power vs commercial by tapping the line side of an ATS switch with a 30 amp disconnect fused at 10 amps to supply a relay. we are relocating the ATS 30 feet away and they have incorporated into the design moving that disconnect to the new location leaving the relay/enclosure in the original location which they interpret from article 240.21(B) (1) that the TAP rule does not allow for the disconnect to be over 10 ft away.. I am in the process of getting approval to redesign the circuit to get the indication from an auxiliary contact instead of tapping the line side of the switch but am curious how this is kosher. shouldn't the disconnect be located 25 feet or less from the relay or at least in sight? the fused disconnect is protecting the relay, not the ATS. me thinks the interpretation is backwards. I read the code 240.21 (B) (4) (4)to apply here??