J jonny1982 Guest Feb 13, 2015 #1 What is the minimum distance a 120/208 3 phase panel needs to be away from a water heater in a commercial application? Code references please. Thanks
What is the minimum distance a 120/208 3 phase panel needs to be away from a water heater in a commercial application? Code references please. Thanks
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Feb 13, 2015 #2 There is no code reference. As long as you meet 110.26 you are good to go
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Feb 13, 2015 #3 Dennis Alwon said: There is no code reference. As long as you meet 110.26 you are good to go Click to expand... agree ! as long as the panel has the 110.26 required clearance the heater can be 1/64 of an inch to the side of the panel.
Dennis Alwon said: There is no code reference. As long as you meet 110.26 you are good to go Click to expand... agree ! as long as the panel has the 110.26 required clearance the heater can be 1/64 of an inch to the side of the panel.