Last summer I posted about a customer of mine who has a building with what appears to be a 400A service (feeders are sized for such) with parallel fuses in the main disconnect with a combined total rating of 800A per leg (2x400A fuses per leg).
We decided to put a logger on the service in the wintertime, when the owner feels that the heaviest load is present from electric heat in the apartments. I set up an Amprobe DM III last Wednesday evening and it ran until this morning. Based on those readings, it looks like the load peaked at L1 - 371A and L2 - 379A.
I'm not very familiar with how fuses as mains react to loads, so my question is, would replacing the parallel 400A fuses with 200A fuses put the residents in danger of blowing a fuse with those loads?
Any thoughts?
BTW, based on a recommendation from someone here on the forum, I rented the unit through Dave Gibson with Intellirent. Excellent support and service!
We decided to put a logger on the service in the wintertime, when the owner feels that the heaviest load is present from electric heat in the apartments. I set up an Amprobe DM III last Wednesday evening and it ran until this morning. Based on those readings, it looks like the load peaked at L1 - 371A and L2 - 379A.