Derating in larger conduit

Status
Not open for further replies.

electricg

Member
Location
wa
Does anyone know if there was ever an exception or different derating percents in the past when using larger conduits? For example, you have 9 #12s in 1/2" conduit (70% derate) vs having 9 #12s (still have to use 70% derate) in 2" conduit? If it is for heat wouldn't larger conduit be more accommodating of this?
 

iwire

Moderator
Staff member
Location
Massachusetts
How about changing that. ;)

Sure, I just have to open my NEC editing app, make the change and by morning everyone's copy of the NEC will be updated. :D

Kidding aside I think you are correct that it could be changed I just think it would be difficult to write the section and enforce it.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The fact is no matter how large the conduit is the conductors will still be bundled on the bottom. Take a 5' straight piece of 2" conduit. Install 10 #12 conductors in it and they are all bundled atop each other. IMO, a proposal will not get accepted.
 

iwire

Moderator
Staff member
Location
Massachusetts
Standard derating does not apply to cable tray, they have there own much different requirements. I think the same could be applied to lighting filled conduits.

However in the big picture I think it would add much confusion to all conduit installations to fix a rarely occurring problem. :)
 

Carultch

Senior Member
Location
Massachusetts
Standard derating does not apply to cable tray, they have there own much different requirements. I think the same could be applied to lighting filled conduits.

However in the big picture I think it would add much confusion to all conduit installations to fix a rarely occurring problem. :)

What about wire troughs and wire trays?

There is a rule that allows you to neglect derates up to 30 wires. Once you put the 31'st wire in it, does that all of a sudden get derated to 40%?
 

Smart $

Esteemed Member
Location
Ohio
What about wire troughs and wire trays?

There is a rule that allows you to neglect derates up to 30 wires. Once you put the 31'st wire in it, does that all of a sudden get derated to 40%?
Yes for wireways, but only in the section where the number of conductors exceed 30, not necessarily the entire wireway.

Wire tray falls under cable tray requirements, which differ from 310.15(B)(3)(a) derating.
 

Carultch

Senior Member
Location
Massachusetts
Yes for wireways, but only in the section where the number of conductors exceed 30, not necessarily the entire wireway.

Wire tray falls under cable tray requirements, which differ from 310.15(B)(3)(a) derating.

I think I meant to say, "wire troughs and wireways".

Essentially what I gather is that the 31st wire in an enclosee wiring structure, and all the others with it are suddenly derated from 100% at 30 down to 40% at 31. Except in Massachusetts.
 

electricg

Member
Location
wa
I think I meant to say, "wire troughs and wireways".

Essentially what I gather is that the 31st wire in an enclosee wiring structure, and all the others with it are suddenly derated from 100% at 30 down to 40% at 31. Except in Massachusetts.

So what is it in Massachusetts?
 

iwire

Moderator
Staff member
Location
Massachusetts
.

Essentially what I gather is that the 31st wire in an enclosee wiring structure, and all the others with it are suddenly derated from 100% at 30 down to 40% at 31.

No that is incorrect. It is the 31 st wire in one cross section that triggers the requirement.
 

Carultch

Senior Member
Location
Massachusetts
So what is it in Massachusetts?

Massachusetts has amendments to the NEC, one of which includes an override table for the bundling derate factors.
http://www.mass.gov/eopss/docs/dfs/osfm/cmr/527cmr12-00.pdf

1-3 = still the same
4-6 = still the same
7-24 = 70%
25-42 = 60%
43 and more = 50%

Hell if I know what the heck they did to justify this table. The last time I checked, the laws of electricity and heat transfer work exactly the same everywhere in the entire world.

I wonder if ampacities would need a major adjustment for use in an airless environment, and evacuated conduit. Because the wire looses its convection for dissipating heat.
 

tom baker

First Chief Moderator
Staff member
How about changing that. ;)

You certainly could make a proposal, as its your idea. You have about 2 1/2 years to get it in. Often a proposal will tell you the intent of the code panel. We have a topic for code changes, do your research first. if you make the proposal with out technical substantiation, it will be rejected.
 

iwire

Moderator
Staff member
Location
Massachusetts
Massachusetts has amendments to the NEC, one of which includes an override table for the bundling derate factors.
http://www.mass.gov/eopss/docs/dfs/osfm/cmr/527cmr12-00.pdf

1-3 = still the same
4-6 = still the same
7-24 = 70%
25-42 = 60%
43 and more = 50%

Hell if I know what the heck they did to justify this table. The last time I checked, the laws of electricity and heat transfer work exactly the same everywhere in the entire world.
.

Better question would be how did the NEC justify changing the table?

Massachessetes still uses the original NEC derating table, when the NEC made the derating more restrictive MA said no, we are not doing that.

You can still find the table MA uses in the annex B of the NEC.

Take a look at Table B.31O.15(B)(2)(11) Adjustment Factors for More Than Three Current-Carrying Conductors in a Raceway or Cable with Load Diversity
 

kwired

Electron manager
Location
NE Nebraska
Massachusetts has amendments to the NEC, one of which includes an override table for the bundling derate factors.
http://www.mass.gov/eopss/docs/dfs/osfm/cmr/527cmr12-00.pdf

1-3 = still the same
4-6 = still the same
7-24 = 70%
25-42 = 60%
43 and more = 50%

Hell if I know what the heck they did to justify this table. The last time I checked, the laws of electricity and heat transfer work exactly the same everywhere in the entire world.

I wonder if ampacities would need a major adjustment for use in an airless environment, and evacuated conduit. Because the wire looses its convection for dissipating heat.
Remember ampacity adjustment is to protect conductor insulation not the conductor itself. A 12 AWG copper conductor can carry 100 amps of current just fine - but will see an increase in temperature that will damage common thermoplastic insulation types.

Put the conductor in a vacuum, you still possibly have thermal melt down effects on that insulation, and maybe at a different temperature then when not in a vacuum but you will not have any oxidation related break downs.
 