electricalist
- dallas tx
A copper line can be a grounding electrode with conditions?
Could RMC ?
Could RMC ?
Qualifies as a pipe electrode. See 250.52(A)(5)(a).A copper line can be a grounding electrode with conditions?
Could RMC ?
If you bury it to an 8' or greater depth somewhere along the way, sure it'll qualify as an electrode...So if i have a service outside of a structure and from a panel [service panel] run rmc to a detatched structure for a sub panel will the rmc be accepted for a gec at the service or the subpanel or a egc to the subpanel or either.
And thats why nobody does it.If you bury it to an 8' or greater depth somewhere along the way, sure it'll qualify as an electrode...
...otherwise, just an EGC.
Was there ever an exception that one could lay a ground rod horizontal if for some reason it couldnt be driven straight down....?
So does that qualify my nec to a garage as a gec....technically no I'm sure, but if it It will still do the job then underground rec conduits should qualify at 3'
That was added in 2011... but made less restrictive in 2014 (exception added).I suppose if you had rock bottom such that the requirements for placement were met, but I think there is another problem: There is new wording saying an EGC cant be a GEC (I am pretty sure on that but I cant find it right now). So does that mean you could if you had a wire EGC installed but not if you were using the RMC as the EGC?
250.121 Use of Equipment Grounding Conductors. An
equipment grounding conductor shall not be used as a
grounding electrode conductor.
Exception: A wire-type equipment grounding conductor installed
in compliance with 250.6(A) and the applicable requirements
for both the equipment grounding conductor
and the grounding electrode conductor in Parts II, III, and
VI of this article shall be permitted to serve as both an
equipment grounding conductor and a grounding electrode
conductor.
Yet a copper water line can be only 2' deep and still be an electrode.
I think the assumption at the time those rules were written was that the metal water line was part of a metal water distribution system that could be several tens of feet long to miles long and likely connected to the electrical systems of many other services.
This is the same reason a metal water line requires a 'full size' GEC.
Yes sir.E, we are glad to help but open the code book and take five minute to read 250.50 through 250.70.![]()
While reading my 2014 handbook I came across detached building and the egc requirements and thought. In the bigger picture if RMC was ran between them it could complete a bigger ges by offering a grounding electrode that bonds that at nearest entrance. With cold water going to RMC at sub panel.....