I would appreciate any comments on the surge testing of motors. I have never done this myself and the test equipment is not cheap. I am also frustrated with my current test methods
which are a megger and a meter. I have had a few motors fail recently with VFD phase to phase faults. With the megger I could not see any problem with the motor, with both phase to
phase and phase to ground insulation testing. But the drives picked it right up, making the drive essentially a piece of test equipment. But when these situations come up and we cannot
verify a bad motor, we then have to verify the VFD also...it wastes a lot of time. It looks like surge testers run from $2K to $15K or more. The selling point here is putting critical motors
on a periodic testing schedule. Thoughts anyone?
As for the meggers, how high should the reading be to call it good?
Thanks