Does anyone know why its allowed to upsize a breaker for one receptacle, but not for more than 1 in 240.4(B)(1)? What was the theory or reasoning behind this?
As I understand it, most receptacles are duplex receptacles so if you are using this then you would not be able to upsize even when it's border line.
for example, #10 wire derated at 70% because of 9 ccc in conduit puts it at 28 amps. Circuit has to be protected at 20 amp breaker not 30.
As I understand it, most receptacles are duplex receptacles so if you are using this then you would not be able to upsize even when it's border line.
for example, #10 wire derated at 70% because of 9 ccc in conduit puts it at 28 amps. Circuit has to be protected at 20 amp breaker not 30.