RCBob
- Arizona, United States
This question concerns conductors for street lighting systems that use 120V, 240V, or 480V power. Can someone please confirm or correct my understanding as written below, and answer the questions?
120V/240V
For a 120V street-light system, conductors are (1) phase (hot), (1) neutral, and (1) bond. Current on the neutral conductor is the same as on the phase conductor, so for voltage-drop calculations and sizing conductors, use the sum of the lengths of both conductors, that is, the two-way distance.
For 240V street lights powered by 3-wire, 120/240V, single-phase power, conductors are (2) phase conductors plus a bond conductor. The phases of the two phase conductors are opposite and balanced, so there would be no current in a neutral conductor, so a neutral conductor is not used. A bond conductor is used. Questions:
240V/480V
Let?s say that the power available is not 3-wire, 120/240V, single-phase, but instead 3-wire, 240/480V, single-phase. Are conductors similar to those described above? Specifically:
4.240V:
Any help in confirming or correcting my understanding will be appreciated.
120V/240V
- Is one of the bond conductor?s possible functions to handle any unbalanced load that may occur?
- Should the bond conductor always be the same gauge as the phase conductors?
- Because there is no neutral conductor,a.Do voltage-drop calculations use the one-way distance?
b. Do you cut that one-way distance in half because there are two phase conductors, which together have less resistance than a single conductor?
240V/480V
4.240V:
- Conductors: (1) phase, (1) neutral, (1) bond?
- Voltage drop calculations use two-way distance?
- 480V:
- Conductors: (2) phase, (1) bond?
- Voltage drop calculations use one-way distance?
- Divide one-way distance by two because two conductors have less resistance than one?