The way I read this table is that for a transformers that has a primary current of 9A or less, if I size the primary OCPD at 167% rounded down, then I do not need any secondary protection. But, if do provide secondary protection I can increase the size of the primary OCPD to 250%.
How common is it to see transformers with only primary side protection? For small dry type transformers that are 3KVA or less, is it common to see these without any secondary side OCPD?