320A 3 ph meters are rated 400A non-continuous - correct?
If so it would be nice if the manufacturer's literature said as much.
320A 3 ph meters are rated 400A non-continuous - correct?
If so it would be nice if the manufacturer's literature said as much.
Square D?
Agree on Milbank.
Our POCO's over here make us use a CT can for anything bigger than 200A or 125HP.
125 HP probably being @ 480 volts?
Single phase and 3 phase Class 320 meters are built for a 400A meter socket, which is rated at 80%, thus 320A continuous. The service is still called 400A. Meter manufacturers came out with them a few years ago, but most utilities (including ours) still require CT's if over 200A 3 phase. We still use CT's because we can use one Class 20 meter for any size service by changing CT's. Cuts down on inventory.