Does bonding of equipment of services (bonding bushings around impaired knockouts) also encompass separately derived systems?
IMO, yes the separately derived system should follow the bonding requirements of 250.92 assuming the voltage is less than 250 to ground
250.92 Services.
(A) Bonding of Equipment for Services. The normally
non?current-carrying metal parts of equipment indicated in
250.92(A)(1) and (A)(2) shall be bonded together.
(1) All raceways, cable trays, cablebus framework, auxiliary
gutters, or service cable armor or sheath that enclose,
contain, or support service conductors, except as
permitted in 250.80
(2) All enclosures containing service conductors, including
meter fittings, boxes, or the like, interposed in the service
raceway or armor
A supply-side [equipment] bonding jumper is required for a separately derived system. There is no equivalent requirement for services.IMO, yes the separately derived system should follow the bonding requirements of 250.92 assuming the voltage is less than 250 to ground
Did you mean another section in 250?
No I realized that was for services but I see a separately derived system as a service (in a sense) That's why I stated IMO. I could not find a code that directly linked a sep. derived system but it seems that it should follow 250.92.
If a separately derived system is not considered a service the 250.92 applies. Why does every sep. derived trany need connection to the gec? Seems to IMPLY what I am thinking.
If a separately derived system is not considered a service then 250.92 applies. Why does every sep. derived trany need connection to the gec? Seems to IMPLY what I am thinking.
250.90 General. Bonding shall be provided where necessary
to ensure electrical continuity and the capacity to conduct
safely any fault current likely to be imposed.
250.96 Bonding Other Enclosures.
(A) General. Metal raceways, cable trays, cable armor,
cable sheath, enclosures, frames, fittings, and other metal
non?current-carrying parts that are to serve as equipment
grounding conductors, with or without the use of supplementary
equipment grounding conductors, shall be bonded
where necessary to ensure electrical continuity and the capacity
to conduct safely any fault current likely to be imposed
on them. Any nonconductive paint, enamel, or similar
coating shall be removed at threads, contact points, and
contact surfaces or be connected by means of fittings designed
so as to make such removal unnecessary.