25v on switch leg

Status
Not open for further replies.
What type of meter did you use to measure this voltage? Is the switch leg still connected to a load and is the load connected to the neutral?
 
Induced or shared

Induced or shared

I am installing low bay HID's, all the old lights are removed. There is nothing on the neutral, 120v on the Hot and somehow 25v on switchleg with the switch off. Any ideas?

If there are long runs of wires could it perhaps be induced voltage? Is it a shared neutral?
 