Transformer low-pressure alarm
texas
Hi all,
I have several 13800/480 V, 1000 kVA transformers at my site. What is your opinion on bypassing the low-pressure alarms on these transformers? They are in a non-corrosive environment, and there are monthly operator rounds to inspect each transformer's pressure level.
I do not really see a purpose for the low-pressure alarm for anything other than detecting leaks. I do not expect a leaking transformer to allow for the ingress of air long enough to cause any negative issues if there are monthly operator rounds. Does anyone feel differently?
Thanks
Unless you have an automatic nitrogen system on this transformer to maintain a positive pressure, I don't see the value. Considering the number of blanketed transformers I find under a vacuum due to light loads and cold weather, I think this would be nothing but a nuisance alarm.
Routine inspection and oil-level alarms would be the normal method of leak-detection.
Thanks, John. We do have a nitrogen blanket, but not one that adds additional gas automatically. I expect inspections to notify us of low pressure.
As long as the pressure stays positive you should be OK, however I would sample and do a DGA more frequently to keep an eye on things, that humid Texas air does not play well with the electrical characteristics of your transformer.