kgk1961
Member
- Location
- Georgia, USA
We are installing stainless steel, lockable enclosures inside a corrections facility. The internal equipment is supplied with a 120VAC duplex receptacle mounted inside a handy box and mounted on the backboard assembly that is installed inside this enclosure.
This backboard assembly takes up the entire back of the enclosure. We have installed conduit into the top of the enclosure (per the manufacturer's direction) utilizing the proper connector. We pulled our three (3) #12AWG THHN conductors into the enclosure, formed them along the sides of the enclosure, terminated them to the receptacle, plugged in the backboard equipment, and closed, and locked, the cover (door). In order to form the conductors neatly, we utilized a "fire rated" "loop conduit" (similar to what you would find under the hood of your car) to better manage the conductors inside the enclosure.
The architect has comeback and said that the "exposed conductors" inside the stainless steel locked enclosure has to be in an "approved raceway" such as "sealtite". I disagree because the enclosure is lockable, and accessible to authorized personnel only. Under his assumption, you will need to install sealtite flexible conduit over the conductors inside a disconnecting means from the point of entrance to the termination point.
I need all responses, and code sections to back up your comments whether you agree or disagree.
This backboard assembly takes up the entire back of the enclosure. We have installed conduit into the top of the enclosure (per the manufacturer's direction) utilizing the proper connector. We pulled our three (3) #12AWG THHN conductors into the enclosure, formed them along the sides of the enclosure, terminated them to the receptacle, plugged in the backboard equipment, and closed, and locked, the cover (door). In order to form the conductors neatly, we utilized a "fire rated" "loop conduit" (similar to what you would find under the hood of your car) to better manage the conductors inside the enclosure.
The architect has comeback and said that the "exposed conductors" inside the stainless steel locked enclosure has to be in an "approved raceway" such as "sealtite". I disagree because the enclosure is lockable, and accessible to authorized personnel only. Under his assumption, you will need to install sealtite flexible conduit over the conductors inside a disconnecting means from the point of entrance to the termination point.
I need all responses, and code sections to back up your comments whether you agree or disagree.