Fordean
- New Jersey
- Electrical Contractor
any good videos out there showing measurements, And Hydraulic benders
If you're doing this offset with a hydraulic bender, which, and what is the shoe's bend radius?any good videos out there showing measurements, And Hydraulic benders
Chapter 9 Table 2 just state radius. I always took that to mean centerline radius, because that how all radii for conduit bends are given to my knowledge....A 2.5" conduit requires a bend radius of 10.5". A 2.5" conduit is approximately 3" in OD. The centerline bend radius is Rcl=12"
I didn't check your formula, but I'm sure someone will appreciate your work.An offset bend has a sweep of angle A, and then a sweep of angle A in the opposite direction.
The offsets are 2*Rcl*(1 - cos(A)) + straight*sin(A).
The total length of straight conduit within the bent region is 2*Rcl*A*pi/180 + straight.
The height of the swept section of conduit is 2*Rcl*sin(A) + straight*cos(A)
BTW "shrink" is the difference between original straight conduit length and final length after bending, i.e. the length lost as a result of bending the offset.
I didn't check your formula, but I'm sure someone will appreciate your work.![]()
I usually go here, to get the NEC requisite bend radii. Your bend radius might be bigger, depending on the tool you use.
http://www.lanshack.com/DesigningConduitRuns.aspx
The maximum bend angle, with no straight section between bends, is 29 degrees. Sticking to common bend angles, you are looking at 22.5 degree bends, with a 3" straight section between the two bends. The total length of 12.5 inches of initially straight conduit used in these sweeps. The total height within the swept region is 12 inches.
You'll hear the term shrink, in regards to offsets. In this example, the conduit shrink is 0.5 inches. This is the initially straight length, minus the height.
Here's a picture of what this sweep looks like drawn to scale. ITS HUGE!
I didn't coin the slang term, but I agree it really isn't lost. It is only 'lost' from the 'run' length.I wouldn't really say that it is lost. ...
I think you better check your references. I don't have access to the full standards, but industry publications lead me to believe table values are centerline radius....
It turns out that if you check standard factory sweep fittings, that the inner radius matches the bend radius table in the NEC. The datasheets of flexible LFMC and LFNC also match this concept.
You can't get it from the factory or shop either! That's why I said OP'er was probably looking at not more than 10? bends in my first post to this thread.This picture is also a good example of a bend we cannot make in the field due to the limitations of the bending equipment.
It is not possible to make back to back bends that close together.
As it works out, the maximum angle for a 3" offset of 2-1/2" EMT on an 881 is just over a 16?.You can't get it from the factory or shop either! That's why I said OP'er was probably looking at not more than 10? bends in my first post to this thread.
Just out of curiosity, I used manual information to extract an approximate minimum straight section between bends of 6-1/2" on a Greenlee 881 using the 2-1/2" shoe.
The best you can do if you don't have the bender is to 'extract' the information from the user manual.Does there exist a table of standards for what bend arrangements *are* physically possible to make in the field?
Given conduit type and trade size, how does one who has never had practical experience with a bending tool, draw a conduit run with bends? What is the table that shows the minimum straight section that surrounds the bend, the distance between bends, and the bend radius with an objective definition of how it should be measured?
Let me know if want to know how.The best you can do if you don't have the bender is to 'extract' the information from the user manual.
well, you are offsetting the thickness of the pipe, so you need to put a
dog leg level on the pipe, put a little scooch in it, flip it over, and put another
little scooch in it, and that'll be about 3 1/8" center to center. just eyeball it.
sight down it, and you want the bottom of the shoe to line up with the oppsite
edge of the pipe...
bend it long and cut to fit, and off you go.
and don't rent a bender to do it. i rented a bender to bend 2" GRC this
last weekend, and the only one i could find available was from these
crackheads in gardena. it made two 90's, and the primary sprocket
exploded in pieces on the third 90.
Well, THAT was a productive day. Hope you had a plan "B".