First off it is not a service it is a feeder.
To me it looks like there is an existing 800 amp panel owned by the landlord.
The new work requires a 350 amp breaker be installed in the landlords panel, a set of 500s run to the new MDP that contains a 350 amp main cb.
I would call this a 350 amp feeder.
The panel board has 5 different breakers on it. The one leading to this suite has 800 printed on the handle. Thats why I thought it was an 800A feed(service) to this suite.
408.36 Overcurrent Protection. In addition to the requirement
of 408.30, a panelboard shall be protected by an
overcurrent protective device having a rating not greater
than that of the panelboard. This overcurrent protective device
shall be located within or at any point on the supply
side of the panelboard.
I apologize for not giving you enough info.
Im learning here. Still pretty new to maintenance.
The panelboard is rated to 1600A.
The 800A breaker is just for this suite.
I just didnt get why the panel in the suite "MDP" is only 350A. Shouldnt it be 800A panel since it's an 800A feed to the suite?
Could be an 800A breaker in roof panel. Drop to the suite MDP would be a feeder tap. But the #3 EGC is an indication it is not....
The print shows a feeder from the roof panel to the MDP that is rated 380 amps not 800.
The feeder has just four - 500 kcmil (I will assume copper) and they are rated 380 amps. The largest breaker allowed would be a 400, not even close to 800.
Could be an 800A breaker in roof panel. Drop to the suite MDP would be a feeder tap. But the #3 EGC is an indication it is not.
View attachment 12093
Good evening. Can you tell me if this is 800A or 350A service.I thought 800A. Thank you.
I apologize for not giving you enough info. Im learning here. Still pretty new to maintenance. The panelboard is rated to 1600A. The 800A breaker is just for this suite. Thats why I think it's 800A feed. I just didnt get why the panel in the suite "MDP" is only 350A. Shouldnt it be 800A panel since it's an 800A feed to the suite? Or is the panel only rated for the max load the suite is putting on the circuit. So if that only 350A panel, does that mean there is still 450A available for use on that circuit?
View attachment 12100View attachment 12101Here is the panel mounted on the roof. The 3rd one down is it. When I throw it it shuts down "MDP,A, and RTU 2" located in the suite. The breaker has 800A labeled on it. MDP is labeled and show on the print 350A. Why is there a 350A panel feed from a 800A. If this 800A breaker on the roof feeds 2 suits then would only 400A be available to each suite? That would explain the 350A "MDP" panel. This is a great discussion. Thank you.
The 3rd one down is it. When I throw it it shuts down "MDP,A, and RTU 2" located in the suite.
The breaker has 800A labeled on it. MDP is labeled and show on the print 350A. Why is there a 350A panel feed from a 800A.
If this 800A breaker on the roof feeds 2 suits then would only 400A be available to each suite? That would explain the 350A "MDP" panel. This is a great discussion. Thank you.
Can't read it in picture. It's the number in the little 'window' off to side of handle.View attachment 12100 ... The breaker has 800A labeled on it...