Hello all,
Two 3 phase 480 Volt machines- (50Amp air compressor and 13Amp air dryer)
I intend to wire 2 machines from a single 100Amp breaker.
I will go from panel about 2 feet into a small wire way (4x4x48" troffer) with #3 AWG CU. I will use Polaris 3 position connectors and splice two taps to each conductor. #10 AWG CU and #6 are the tap sizes.
the taps will be no more than 3 feel long and will terminate in fused discos with 70Amp and 15Amp current limiting fusees (MOCPD per nameplates.)
#8 AWG CU will be used for grounding/ bonding to the disconnects.
Both ground and conductors will be reduced on the load side of the disconnects (sized per breaker / load)
My EMT will be bonded for circuits over 151 Volts.
Thank you for the input!!