Section 110.21(B) ?Field-Applied Hazard Markings?
Electrical systems in general, and PV systems in particular, require numerous plaques, labels, directories and signs. In practice, the materials that contractors use for field-applied signs or labels range from the clearly inadequate (laminated paper used in outdoor locations) to exemplary (engraved metal). Further, different contractors and facility operators tend to use different styles for labels, in terms of both the label color and the text color, size and font.
While field-applied labels and signs are inherently project and application specific, Section 110.21(B) seeks to standardize marking requirements for improved safety. The intent of the new language is to more effectively identify and communicate potential hazards in the field by improving the consistency with which Code-mandated hazard labels are deployed. In effect, these labels must provide adequate warning, be permanently affixed and be sufficiently durable.
Per Section 110.21(B)(1), field-applied hazard markings ?shall adequately warn of the hazards using effective words and/or colors and/or symbols.? Per 110.21(B)(2), the label ?shall be permanently affixed to the equipment or wiring method.? While this section also states that hazard markings in general ?shall not be handwritten,? an exception is provided for specific portions of the label or marking that are variable or subject to change. Lastly, per 110.21(B)(3), the label ?shall be of sufficient durability to withstand the environment involved.?
Note that labeling and marking requirements found throughout the Code?including many of those in Article 690?now refer back to Section 110.21(B). While the adequacy and durability of field-applied hazard markings is potentially subjective, two informational notes in this section refer to the American National Standard for Product Safety Signs and Labels (see Resources), otherwise known as ANSI Z535.4-2011, for application guidelines. This standard includes guidelines for appropriate colors based on signal words such as ?Danger,? ?Warning? or ?Caution.? It describes the letter style and size required for a label?s signal word panel and message panel, as well as location requirements related to visibility. It also addresses durability, in terms of label life expectancy and replacement requirements. Except where more stringent local requirements apply, AHJs are likely to accept labels and signs designed to meet this ANSI standard.
Todd Fries is a member of CMP No. 4 and the marketing manager for identification systems at HellermannTyton. Regarding material durability, Fries explains: ?The NEC and other codes, like the International Fire Code, do not specify a unit of time that a label must withstand the environment. Typically, these codes simply state that the label must be suitable for the environment where it is installed. This does not mean that the label must last the life of the installation. Everything wears out over time, including PV modules, inverters and other system components. However, Article 10.2.2 of ANSI Z535.4-2011 does state that a label shall be replaced when it becomes unreadable.?
To protect against premature failures and recurring replacement costs, Fries recommends that system integrators request label-material durability information and accelerated aging test data from the product vendor or manufacturer.