What is typical for a hot tub prewire?

Status
Not open for further replies.

arazu

Member
Location
Arizona
My client has no idea what make/model they are going to purchase. Without specs I'm unsure. The company I used to work for would pull 8-2 but that seems low to me.

I was hoping someone who works with hot tubs a lot could offer some advice.

Thanks!
 

FionaZuppa

Senior Member
Location
AZ
Occupation
Part Time Electrician (semi retired, old) - EE retired.
it will most likely be less than 50A 240v
w/o knowing the specs, i would pull NM-8/3 or if conduit 8-8-8-10(gnd)
 

480sparky

Senior Member
Location
Iowegia
Without specs, I wouldn't do anything less than four No. 6s. The price generally tends to help them make a firm decision.
 

arazu

Member
Location
Arizona
Without specs, I wouldn't do anything less than four No. 6s. The price generally tends to help them make a firm decision.

I think you're right about the price helping them decide.

I had no idea some required a full size ground. I was hoping to use 6/3.

Thanks to everyone who responded. You've been a great help.
 