A arazu Member Location Arizona Mar 19, 2015 #1 My client has no idea what make/model they are going to purchase. Without specs I'm unsure. The company I used to work for would pull 8-2 but that seems low to me. I was hoping someone who works with hot tubs a lot could offer some advice. Thanks!
My client has no idea what make/model they are going to purchase. Without specs I'm unsure. The company I used to work for would pull 8-2 but that seems low to me. I was hoping someone who works with hot tubs a lot could offer some advice. Thanks!
mgookin Senior Member Location Fort Myers, FL Occupation Retired inspector, plans examiner & building official Mar 19, 2015 #2 The size of the heater and the pump are a function of the size of the tub. Check with these guys; they have everything: http://therecreationalwarehouse.com/
The size of the heater and the pump are a function of the size of the tub. Check with these guys; they have everything: http://therecreationalwarehouse.com/
FionaZuppa Senior Member Location AZ Occupation Part Time Electrician (semi retired, old) - EE retired. Mar 19, 2015 #3 it will most likely be less than 50A 240v w/o knowing the specs, i would pull NM-8/3 or if conduit 8-8-8-10(gnd)
it will most likely be less than 50A 240v w/o knowing the specs, i would pull NM-8/3 or if conduit 8-8-8-10(gnd)
S sefs Member Location Gibsonia, PA Mar 19, 2015 #4 Beware: Many installation manuals require a "full sized ground" (same gauge as line conductors) as well as only copper conductors.
Beware: Many installation manuals require a "full sized ground" (same gauge as line conductors) as well as only copper conductors.
C Cow Senior Member Location Eastern Oregon Occupation Electrician Mar 19, 2015 #5 FionaZuppa said: it will most likely be less than 50A 240v w/o knowing the specs, i would pull NM-8/3 or if conduit 8-8-8-10(gnd) Click to expand... I'd also estimate 50 amps or less. But, I think you meant 6-3 NM since 8-3 NM is only rated for 40 amps.
FionaZuppa said: it will most likely be less than 50A 240v w/o knowing the specs, i would pull NM-8/3 or if conduit 8-8-8-10(gnd) Click to expand... I'd also estimate 50 amps or less. But, I think you meant 6-3 NM since 8-3 NM is only rated for 40 amps.
480sparky Senior Member Location Iowegia Mar 19, 2015 #6 Without specs, I wouldn't do anything less than four No. 6s. The price generally tends to help them make a firm decision.
Without specs, I wouldn't do anything less than four No. 6s. The price generally tends to help them make a firm decision.
A arazu Member Location Arizona Mar 19, 2015 #7 480sparky said: Without specs, I wouldn't do anything less than four No. 6s. The price generally tends to help them make a firm decision. Click to expand... I think you're right about the price helping them decide. I had no idea some required a full size ground. I was hoping to use 6/3. Thanks to everyone who responded. You've been a great help.
480sparky said: Without specs, I wouldn't do anything less than four No. 6s. The price generally tends to help them make a firm decision. Click to expand... I think you're right about the price helping them decide. I had no idea some required a full size ground. I was hoping to use 6/3. Thanks to everyone who responded. You've been a great help.