mwm1752
 - Aspen, Colo
Would you consider a cam-lok receptacle mounted on the generator frame as compliant with 250.34(B)(2) if
1- Feeding a hardwired temp panel mounted on unistrut with branch circuits attached to 120v receptacles?
2- Feeding a plug in temp power unit the has 120v receptacles intergal to the unit?
3- Or none of the above as the cables are not bundled as a cord set to the equipment.
250.34 Portable and Vehicle-Mounted Generators
(B) Vehicle-Mounted Generators. The frame of a vehicle shall not be required to be connected to a grounding electrode as defined in 250.52 for a system supplied by a generator located on this vehicle under the following conditions:
(2) The generator supplies only equipment located on the vehicle or cord-and-plug-connected equipment through receptacles mounted on the vehicle, or both equipment located on the vehicle and cord-and-plug-connected equipment through receptacles mounted on the vehicle or on the generator, and