A new facility in the area will be served by the POCO and metered by them on the primary. Three CTs and three PTs, owned by the POCO.
Before the year is up the primary voltage from the POCO will convert from 12.4/7.2Y to 25/14.4Y. The thinking is that at the start the meter set will need dual voltage PTs and the customer that is providing his privately owned transformer will need a dual voltage high side on his transformer. Customer doesn't have a choice in this situation if he wants power before the primary voltage conversion.
I am thinking on the metering side that the 14.4 PTs could be installed from the start, never change when the primary line converts and still be able to accurately measure the customer's usage usage from the metering set. The CT's do not require a voltage and would be installed with an insulation rating for the higher voltage. In the short run while the line is 12.4, The PTs would produce only 60 volts as compared to the normal 120 because of the fixed turns ratio in the PTs. My math shows the net KW from volts X amps to equal at the metering set before and after the voltage conversion. This does not figure in PF but now my head hurts and I am going to stop thinking about it for a while.
What else should I be looking at? I am not the meter guy and delivery time for the dual voltage PTs is the only reason I am thinking like this.
Thanks
Thanks