Transformer - 480V 1KA
Hi,
I have a single phase primary, 480V 1KVA transformer and three phase secondary 240V/120V. My question is, does code require me to fuse the secondary side of the transfomer? I have sized the fuse protection for each device that is connected on the secondary side. I have a 120V cooling fan, 1A - 120V receptacle, 2A and 240V control power for a servo drive, 4A. Do I need additional protection in front of these fuses on the secondary side of the transformer?
Thanks,
Kilowatt76
...I have a single phase primary, 480V 1KVA transformer and three phase secondary 240V/120V. ...
Take a look at the transformer again. If it is a single phase primary, it is a single phase secondary. Perhaps the transformer is two wire 480V primary, and a three wire 120/240 secondary.
ice
ice
I'm glad you noticed that.
I thought I was fixing to learn something new. :)
JAP>