We are wiring a new building with a fire pump.
The Service entrance conductors to the combination fire pump controller/ATS come from the utility transformer.
This firepump is backed up by a generator which serves other loads in the building. The fire pump circuit breaker is isolated from the other breakers in the generator.
My question is on the grounding/bonding. We are not switching the neutral on the other transfer switches in the building, so the bonding jumper is removed in the generator.
Next to the fire pump breaker in the generator there is a second bonding jumper and the question is do we need to pull a grounded conductor and no grounding conductor from the generator to the fire pump controller/ATS, or can we remove the bonding jumper at the generator and just utilize an equipment grounding conductor.
We installed a grounded conductor from the utility transformer. to the ATS/controller.
Thanks in advance for the help.
Bob
The Service entrance conductors to the combination fire pump controller/ATS come from the utility transformer.
This firepump is backed up by a generator which serves other loads in the building. The fire pump circuit breaker is isolated from the other breakers in the generator.
My question is on the grounding/bonding. We are not switching the neutral on the other transfer switches in the building, so the bonding jumper is removed in the generator.
Next to the fire pump breaker in the generator there is a second bonding jumper and the question is do we need to pull a grounded conductor and no grounding conductor from the generator to the fire pump controller/ATS, or can we remove the bonding jumper at the generator and just utilize an equipment grounding conductor.
We installed a grounded conductor from the utility transformer. to the ATS/controller.
Thanks in advance for the help.
Bob