I am an HVAC technician(15 yearss experience) who is familiar with the NEC specifically related to HVAC equipment installations. I have been taught, and the NEC dictates this in most cases that I am aware of, that conduit bodiess are purpossed for wwire pulling and not splicedd connections. However, I run into situations where a feed to for example, a rooftop package heating and cooling unit has a splice at the end of the run in a conduit body connected to MC run through the roof and to an equipment disconnect. I just failed an inspection on an install of a 5 ton condensing unit on a roof wherein we did not insstall new electric but switched out old equipment for new. The 2" metal conduit alreeady in place ended on the roof at an LB and the old unit's wiring went from a disconnect into the LB and spliced inside it. The new equipment was installed, new disconnect attached to it and flexible condduit run to the LB and wires spliced inside. The inspector failed it based on that splice. Technically correct, but I am always a bit mystified on being failed on pre existing wiring. I expected he would fail or pass only based on the neww equipment and not existing wiring. My question is, is this something an EI will generally always fail in your experience or will some allow that splice since it is connectedd to existing wiring/conduit body? If it is an abssolute that it cannot be spliced in the pre existing LB, can the LB simply be switched out for a def purpose splice box attached to the end of the conduit where it comes through the roof? Not sure how to correct this other than removing all old #6 from condit back to panel and pulling new runs of #6. Thanks.