Yes, doing a panel change. The GEC was 4" to short to make it to the neutral bar. For now, we just tapped in a 2 hole lug up high and landed the GEC in it. I was curious if I could do this and run an equivalent sized bonding conductor out of the other hole 4" to the neutral bar ???
I was trying to use this somehow
| 250.64(C) Continuous. Except as provided in 250.30(A)(5) and (A)(6), 250.30(B)(1), and 250.68(C), grounding electrode conductor(s) shall be installed in one continuous length without a splice or joint. If necessary, splices or connections shall be made as permitted in (1) through (4): (1) Splicing of the wire-type grounding electrode conductor shall be permitted only by irreversible compression-type connectors listed as grounding and bonding equip-ment or by the exothermic welding process. (2) Sections of busbars shall be permitted to be connected together to form a grounding electrode conductor. (3) Bolted, riveted, or welded connections of structural metal frames of buildings or structures. (4) Threaded, welded, brazed, soldered or bolted-flange connections of metal water piping. |