larmee
- Jackson, TN 38301
Investigated a situation at a local bank involving water seeping out of the conductors inside the switchgear onto the main breaker. The installation has 4 sets of 350 parallel comprising a 1200 ampere service. The installation was initially installed in 2006. There are 4 sets of PVC conduits running from the service pole into the switchgear located approx. 150 feet away. The conduits at the service point have drip loops and are taped and there are loops formed in the conductors inside the gear. No water is visible in the conduits in the raceways or in the switchgear itself. All 4 sets of conductors have water present and corrosion has developed on all the lugs. The neutral lugs are stacked 3 high and one offset and all 4 are corroding as well. I have observed actual water seeping out of the conductors. Besides the obvious that water is inside the jacket any ideas on how it is making its journey around all the bends and loops? The conductor size is 350 type is THHN / THWN. The service is not overloaded with the peak load being 538 amperes since installation.