I have a 300 KVA transformer, dry type electronic transformer.
I expect it to be heavily loaded, for long periods of time. (Maybe even 100% load for 7 days straight).
There will also be some harmonic content in the load current. I've been told 100KVA is for 6 pulse rectifiers with a 39% THD.
The other 200KVA is for low power electronics, and AC motors. I'll have to make a guess at the harmonics on this.
Is there any way I can calculate if I need a K rated transformer, and if it should be a K-4 or K-13?
Also, is there any way to figure out what temp. rise I should use? I can get a K rated transformer in a 115 deg rise, which would run cooler than the standard 150 deg rise.
I was also considering a standard, non K rated transformer with a 80 deg rise.
Any advice is appreciated.