greenspark1
- New England
look up the cover cat number...the catalog says "cover with door is suitable for QO142M200, QO140M225, QO142L225G load centers".
And those are single phase panels.
that would be my guess
I decided some firsthand investigation was in order so took off the cover and was surprised to find a three phase panel!
I'm not sure how this is possible since the trim says it is for single phase panels. I am very surprised.
The other thing I noticed was the phase bus bars don't extend down all the way. You can see this in the photo. Doesn't this mean that poles 21-24 are un-usable since there is no bus there?! Not sure why they would make panels like this.
But there is no guarantee the other panel isn't a single phase panel as that same cover fits multiple loadcenters both single and three phase. Had there been at least one three pole breaker in the first panel then you can fairly safely assume you have a three phase panel without removing the cover.Yes a different panel, but same label on the door. This is from a college campus, 3 separate buildings with 3 similar panels. Good eyes![]()
Are these all 100A main bus, and how can you tell. Per NEC don't panels need to be labeled with their rated voltage/current?
Any insight on why the main bus doesn't extend down to all the poles? :?
Thanks for the feedback.
PS: here's this panel's label:
The actuall supply voltage labeling is a responsibility of the installing electrician, not the manufacturer of the panel. The manufacturer just needs to list the maximum rated value.Per NEC don't panels need to be labeled with their rated voltage/current?
The purchaser of the equipment wanted the lowest possible price, so they only wanted bus bars space for 20 circuits instead of 24.Any insight on why the main bus doesn't extend down to all the poles? :?