Are non-fused safety switches reqruied to be provided with "series rated" labeling per the NEC where applied in applicaitons whree the fault current exceeds 10kAIC? In looking through different manufactures literature [Sq.D, Siemens, etc.] they all state that the non-fused safety switch is rated for 10kAIC [Short cirucit current rating, really a withstand rating not an interrupt rating]. However each manufacturer also list higher ratings based on specific OCPD ahead of the safety switch [see attached excerpt from a Siemens Document]. The standard safety switch is rated for 10kAIC for any UL breaker, however only 18 & 25 with listed Siemens breakers as the OCPD or higher [200kIAC] with the listed fuse type. If the switch is applied where the avaliable fault current is greater than 10kAIC and the upstream breaker allows for an 18kAIC rating [per the manufacturers chart] or even the 200kAIC if fuses are used upstream is the safety switch requried to be labeled with a "series rated" label indicating the series rating with the upstream OCPD? The NEC [110.22] talks about equipment enclosures for circuit breakers or fuses applied in compliance with series combination ratings ? ? Shall be marked in the field as directed by the engineer to indicate the equipment has been applied with a series combination rating.? And it goes on to provide examples of labels. however the non-fused safety switch is not an "enclosure for cirucit breakers or fuses".??:?