M Matt Mckenzie Member Location United States Apr 13, 2015 #1 Branch circuit you size to the load and breaker with next standard size. Same for a feeder?
ActionDave Chief Moderator Staff member Location Durango, CO, 10 h 20 min from the winged horses. Occupation Licensed Electrician Apr 14, 2015 #2 Short question. Short answer 215.3 takes you to 240. After that it's all about the details.
Smart $ Esteemed Member Location Ohio Apr 14, 2015 #3 Matt Mckenzie said: Branch circuit you size to the load and breaker with next standard size. Same for a feeder? Click to expand... 800A and less, yes. 215.2 for minimum feeder conductor size. 215.3 for minimum feeder conductor OCPD.
Matt Mckenzie said: Branch circuit you size to the load and breaker with next standard size. Same for a feeder? Click to expand... 800A and less, yes. 215.2 for minimum feeder conductor size. 215.3 for minimum feeder conductor OCPD.