I have a quick question regarding the requirements for cable tray spare space requirements and the relationship with article 392 in NEC. We have a company requirement to keep 20% spare space in addition to 20% spare cabling already included with the mutli-pair home-run cables.
If I correctly understand NEC article 392, it mandates that 50% of the total cross-sectional area of all the cables be provided as spare space. Of course, this is more stringent than our requirement because we only allow 20% spare space. Remember we in our standards refer to instrumentation cables which are typically very low power/voltage of less than 50 VDC (ITC or PLTC). I feel that 50% in NEC is due to power loading since we deal with high power cables, which is not what we use in Instrumentation applications.
The question here is: does mandating both requirements pose a contradiction?
I have a quick question regarding the requirements for cable tray spare space requirements and the relationship with article 392 in NEC. We have a company requirement to keep 20% spare space in addition to 20% spare cabling already included with the mutli-pair home-run cables.
If I correctly understand NEC article 392, it mandates that 50% of the total cross-sectional area of all the cables be provided as spare space. Of course, this is more stringent than our requirement because we only allow 20% spare space. Remember we in our standards refer to instrumentation cables which are typically very low power/voltage of less than 50 VDC (ITC or PLTC). I feel that 50% in NEC is due to power loading since we deal with high power cables, which is not what we use in Instrumentation applications.
The question here is: does mandating both requirements pose a contradiction?