Pierre C Belarge
- Westchester County, New York
(QCRV)ul - specifically Reducing Washers.
"Metal reducing washers are considered suitable for grounding for use in circuits over and under 250 V and where installed in accordance with ANSI/NFPA 70 "National Electrical Code." Reducing washers are intended for use with metal enclosures having a minimum thickness of 0.053 in. for non-service conductors only."
(quote from UL White Book)
As I read this, it tells me that reducing washers are not to be installed with service conductors.
Reading the IAEI 2011 Analysis Book, page 107, the author states that, " Reducing washers are evaluated and listed for grounding for non-service conductors only."
I do not read it to say what the author has stated, I read it to say that reducing washers are not suitable for use with service conductors.
What are your opinions?
Does anyone have a link(s) that point to more information about installation of reducing washers?
Thanks
Thanks