HNS
Member
- Location
- dayton, ohio
Hello i am new here but looking for a little insight from peers. I am currently upgrading a service from 200a to 400a (320). The existing UG service was installed in 2008 4/0-4/0-2/0 Al URD. i am proposing to dig along side of existing adding another 4/0 URD to utility pole to supply the new 400a meter base with parallel 4/0. My inspector says he has never seen it done like this and would have to research. Does anyone see a problem with this?