How about the quality of the return connection from workpiece to welder? No need to involve " ground", and having any of that current trying to travel via earth (dirt) or EGC can cause problems.The first two things I would check are:
1. The quality of the ground connections between the work and the welding machine.
2. Voltage drop on the power supplying the welding machines while they are operating.
That's what I meant by item #1: the "work cable" which is connected to the workpiece and provides the return current path from the workpiece to the welding machine. Among welders, that's commonly referred to as the ground clamp or the ground connection.How about the quality of the return connection from workpiece to welder? No need to involve " ground", and having any of that current trying to travel via earth (dirt) or EGC can cause problems.
. Checked cord connections, voltage input
#1: the "work cable" which is connected to the workpiece and provides the return current path from the workpiece to the welding machine.
The votage drop while running is only 2V and 3V on some at worst.
The ground clamp connection is good as well because they are actually permanently attached because the welding tables are so large.
Both wire feed and stick welders are suffering from the same problems though! I'm really confused on this one.
I have no idea how much impact this may have but is it possible high harmonics can be a problem?
Maybe need to look closely at both voltage and current and see if something is abnormal.
Does the problem occur when only one welder is in use and the others are powered off? Did you perform your voltage drop tests when only one welder was in use?The voltage drop I took is at the welder input. The welding return connection is good. There are no VFD in the shop just a ton of welders. It seems weird that multiple welders would suffer from the same problem so maybe there is an issue with the power quality. What's the next best step to addressing this problem? The shop is on the utility
Does this problem only appear when several welders are in use or does it improve if there is limited welding taking place? If newer vintage machines with electronic controlled output - the more you have going the more potential you have for harmonic issues.The voltage drop I took is at the welder input. The welding return connection is good. There are no VFD in the shop just a ton of welders. It seems weird that multiple welders would suffer from the same problem so maybe there is an issue with the power quality. What's the next best step to addressing this problem? The shop is on the utility