In the older versions of NFPA 70E there was an exception for performing an arc flash risk assessment (formerly known as an arc flash hazard analysis). The exceptions included:
1. The circuit is rated at 240 Volts or less
2. The circuit is supplied by one transformer
3. The transformer supplying the circuit is rated less than 125 kVA.
In the 2015 version in section 130.5 is states that an arc flash risk assessment shall be performed.
Do the same exceptions still apply? If so, can you provide where these exceptions are stated in the 2015 version.
Thanks in advance.