Will Wire
Senior Member
- Location
- California: NEC 2020
- Occupation
- Electrical Contractor
I was called out recently to a rural property (house built in 1974) where the main service is mounted on a pole near the well pump. From the service equipment a three wire feeder in rigid conduit is run to a sub-panel at the house. At the house a ufer ground was installed in the foundation. The ufer ground and the grounded conductor of the feeder terminate on the neutral buss bar, as do all the circuit grounded conductors and equipment grounding conductors. This against what I understand to be correct. The house was built in 1974. Was this a code compliant installation in 1974? Thank you, Trent