non compliant with 110.25 -- what does the panel schedule say?
non compliant with 110.25 -- what does the panel schedule say?
That paragraph refers to locking things in the open position. These set screws lock them in the closed position.
That paragraph refers to locking things in the open position. These set screws lock them in the closed position.
So we should call these lock ons :?
700.12(F)(2)Exception: In a separate and uninterrupted area supplied
by a minimum of three normal lighting circuits that are not
part of a multiwire branch circuit, a separate branch circuit
for unit equipment shall be permitted if it originates from
the same panelboard as that of the normal lighting circuits
and is provided with a lock-on feature.
And often for circuits with mechanical time clocks. As well as circuits for egress lighting and night lighting.Use them for circuit feeding fire alarm panel