mitch cochrell
Is there a video available to educate somebody on corner grounded delta systems? I am providing electrical services at a brand new facililty in Houston. They relocated from an area of town that had 240 volt delta as the only option for three phase systems. Therefor, all of the existing equipment is 240 volt 3 phase (high leg). The engineer designed the new building with two 480v/240v Delta Delta corner grounded transformers to supply the existing equipment. We had to get UL involved due to The City of Houston ordinance to approve all equipment. The UL representative noticed sometimes you read 140 to ground on all three phases and sometimes you read 240 to ground on two of the phases and 0 to ground on the third. He thinks the company that installed the new system didn't ground the transformers properly and could be a shock hazard and available fault current issues. I have heard of this system but never seen or installed one before. Any help would be greatly appreciated. Thanks