silurian
Member
- Location
- Northern Wisconsin
I am almost strictly a residential electrician, but was recently asked by a local volunteer fire department to advise them about whether their service is big enough for a new breathable air compressor they would like to install. I got the specs, took note of other loads in the building and said I'd do a load calculation and get back to them. It is a Bauer Legacy 13 E1 compressor. Specs: 230 V single phase; full load amps-50; locked rotor/start up amps-300; time delay fuse rating amps-60; circuit breaker size-100. Although I haven't done the load calculation yet, I think adding this load will exceed their 200 amp service. But here is my question which I can't seem to find the answer for in the code book. Can the locked rotor/start up amps (300) of a motor exceed the rating of the service (200 amps)?