I am wondering how exactly it is that a current limiting fuse of greater value than a branch circuit breaker can be used to protect that device, and be used to to increase the short circuit rating of the overall panel. For instance, panelboards often use fuses to take a panelboard full of 14 kA breakers to a much higher rating. In my case, the fuse is larger than the breaker: say 400A J-type CL fuse with 200kA interrupt rating and some generic 40A MCCB, rated for 35 kA.
Here's my issue: since the fuse is much larger than the CB, and presume they are "selectively coordinated," then will we not have an undesirable sequence of operations? I.e. the CB will open before the fuse (desireable for coordination), but will consequently be forced to break a fault above its interrupt rating, say if the bolted fault current is 50kA.
Then again, perhaps I am thinking about it all wrong... let's assume that for the faulted circuit, the fuse and CB are effectively in series. Then that means that the current limiting fuse will act to clamp down on the current passing through this circuit, and the peak let-thru current is what the branch CB will "see." In that case, everything seems fine. But I've plotted the TCC curves on Etap, and indeed the instantaneous trip curve of the CB is about 10X 40A, or 400A, while the fuse will not even start current limiting before 8kA. Using the Etap Star Sequence of Operations function to simulate, indeed the branch CB opens before the main fuse under fault conditions.
To get to the core concept here: is the whole premise that the current limiting fuse keeps the let-thru current safely below the interrupt rating of the branch CB, but that the branch CB will still open before the fuse, even under high fault conditions?
Thanks for the help!
Dave