For bonding a wet pool light niche, does 680 require a #8 Solid insulated or bare copper ground?
N Npstewart Senior Member May 13, 2015 #1 For bonding a wet pool light niche, does 680 require a #8 Solid insulated or bare copper ground?
luckylerado Senior Member Location Lake of the Ozarks May 13, 2015 #2 Insulated 2014 680.23(B)(2)(b) "....Where a nonmetallic conduit is used, an 8 AWG insulated solid or stranded copper bonding jumper shall be installed ....."
Insulated 2014 680.23(B)(2)(b) "....Where a nonmetallic conduit is used, an 8 AWG insulated solid or stranded copper bonding jumper shall be installed ....."
N Npstewart Senior Member May 13, 2015 #3 luckylerado said: Insulated 2014 680.23(B)(2)(b) "....Where a nonmetallic conduit is used, an 8 AWG insulated solid or stranded copper bonding jumper shall be installed ....." Click to expand... Great, thanks!
luckylerado said: Insulated 2014 680.23(B)(2)(b) "....Where a nonmetallic conduit is used, an 8 AWG insulated solid or stranded copper bonding jumper shall be installed ....." Click to expand... Great, thanks!
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) May 13, 2015 #4 Note that for the equipotential bond to the forming shell associated with the wet niche fixture, a bare conductor is o.k.
Note that for the equipotential bond to the forming shell associated with the wet niche fixture, a bare conductor is o.k.